Work method statement for installation of transformers

archdevil

Royal Member
Work method statement for installation of transformers

Introduction (Purpose)
The method statement describes the procedure for Installing and Testing of transformers and Accessories in the following stations:

Sub-Station 1
Sub-Station 2
Fire pump house

Activities (Work Scope)
1. Installation of Transformers
2. Commissioning of Transformers

Reference
Project Safety Plan
Project Environment Plan
Nokia Electrical Tender
E&M works and Materials Specification

Definitions
NOKIA - Nokia Mobile Facility, Chennai
ITP - Inspection and Test Procedure
MP - Management Procedure
PPE - Personal Protective Equipment
HSS - Health and Safety Standard
DWP - Detailed Works Program
N/A - Not Applicable

Specification Clauses
Following Clauses of contracts specification shall be followed

a. Nokia Electrical Tender
b. Relevant Indian Standards

Mobilization Plan
The Sub Contractor will be fully equipped with plant and tools sufficient to carry out all the works.
The sub contractor and his labour force will have under gone a full safety induction course as conducted by the contractor.

Construction Equipment
No Major plant & equipment is required for this activity, minor equipment include as listed below are used for installation of Transformers :

1. Electric Drill
2. Screw Driver
3. Spanner
4. Cutter
5. Crimping tool
6. Pipe rollers
7. Torque wrench
8. Chain –pulley block

Personnel
The personnel on site will be fully competent to carry out all related works associated with the project to the relevant standards.

The site personnel will have attended the required contractors induction safety and/or competency training and will abide by the health & safety plans, policy and procedures.

Materials
All materials used at site should confirm to requirements of environmental policy of the project. The following material will be used for the installation of Transformers and accessories:

1. MS Channel & Angle for support structures

Construction Procedure and Construction Method
1. Support Structure:

a) Fix wheels to take load of Transformer

Electrical system:

a) Selection of size of power cable & control cable based on Transformer rating & Drawings
b) Laying of Trays in already constructed trench for the passage of power & control cable.
c) Laying of cable from Transformer to MDB & from 11 KV Panel room is carried out.
d) Cable termination is carried out at both ends using Thimbles & various other mechanical equipments.

2. Earthing system:

a) Construct the copper clad earth pit using 19 mm dia 3 Mtrs long copper rod for Body & Neutral earthing & its Inspection cover
b) Selection of Size of earthing cable based on Transformer rating & drawings.


Responsibility and Authority

Refer to attachment No: - 1

Statutory Consents
Not applicable

Work Programme
Latest coordinated installation program will be strictly followed and fully complied with.

Quality Assurance
The execution of works will strictly follow the Project Quality Assurance Plan.

Health and Safety Plan
The execution of works will strictly follow the Project Safety Manual

Environment Policy
The execution of works will strictly follow the Project Environment Plan.

Relevant documentation
A. Approved Construction Reference drawings.
B. Relevant Indian Standards

Sub Contractor
ETA Engineering Pvt. Ltd. will work as a sub-contractor.
Address ETA Engineering Pvt. Ltd.,
5th Floor,688,Anna Salai,
Chennai - 600 006.

Risk and Hazard Assessment
Attached.

ITP (Inspection & Test Plan)
As per attached ITP.

Inspection
As per attached ITP

Attachment
Risk Assessment Form
Responsibility and Authority – Attachment no. – 1.

Same procedure is attached in pdf format below
 

Attachments

  • Work method installation of transformer.pdf
    194 KB · Views: 215