1) First and Foremost the structure should have been ensured curing properly.
2 ) As per CPWD Tech., Specfications, if it is nominal mix(1:2:4, 1:1.5:3 & 1:1:2) and concrete specifically done with OPC , the 28 day acceptable limit is upto 70% of the compressive strength. Any thing below 70% needs NDT or DT depending upon the importance of the structure.
3) As per CPWD and IS 456, if it is design mix, the acceptable limit as per IS 456 - Table 11 (as also posted by DNYAN Sir earlier in his postings) analysis needs to be done for mean of 4 overlapping & Individual results.
4) If Point no.-02 is not meeting out , then as per IS 456, if 50 to 60 cube sample results are available we can do Standard deviation.
5) If Point no.-03, is not meeting out , the we have to go for DT or NDT.
6) As per Point no-01, if curing would have been ensured properly, then NDT or DT will meet the criteria.