Why we use 150mm size cube for compressive strength testing.
Hi all civil engineer,
when i was in collage i wonder that all constructions site have the cube size of 150mm x 150mm x 150mm.
IS 516 do mention that we should use 150mm size cube or 100mm size cube as alternative when maximum size of aggregates do not exceed 20mm.
Max construction site have the cube testing machine of capacity 100 ton / 1000kn. and our compressive strength calculation is load / area i.e.- n/mm2
If the loading area increases the load for crushing or load at which it fails also increases.
if you are checking M30 concrete and you requires min. comp strength of 33n/mm2 and the size of cube is 150mm then the load required to get this much strength is 742.5 Kn. if you use cube of size 300mm the load require becomes 2970 kn, this is practically not possible as to crush the cube u require 3000kn/300 ton capacity machine. When the applied load is much more the additional safety factors need to be increase because when cube fails under such loads may hit anything in room with bullet speed.
Also casting of this size cube and handling is not easy.
for feasibility, safety and ease of work we use 150mm size cubes.
if you have a machine with less capacity and load to crush the cube is more than the capacity of machine you can reduce the size of cube further to 100mm.
This you can do when you go for high grade concretes M50 and above and your machine capacity is 100 ton.
Hi all civil engineer,
when i was in collage i wonder that all constructions site have the cube size of 150mm x 150mm x 150mm.
IS 516 do mention that we should use 150mm size cube or 100mm size cube as alternative when maximum size of aggregates do not exceed 20mm.
Max construction site have the cube testing machine of capacity 100 ton / 1000kn. and our compressive strength calculation is load / area i.e.- n/mm2
If the loading area increases the load for crushing or load at which it fails also increases.
if you are checking M30 concrete and you requires min. comp strength of 33n/mm2 and the size of cube is 150mm then the load required to get this much strength is 742.5 Kn. if you use cube of size 300mm the load require becomes 2970 kn, this is practically not possible as to crush the cube u require 3000kn/300 ton capacity machine. When the applied load is much more the additional safety factors need to be increase because when cube fails under such loads may hit anything in room with bullet speed.
Also casting of this size cube and handling is not easy.
for feasibility, safety and ease of work we use 150mm size cubes.
if you have a machine with less capacity and load to crush the cube is more than the capacity of machine you can reduce the size of cube further to 100mm.
This you can do when you go for high grade concretes M50 and above and your machine capacity is 100 ton.