4. Presently I tried to reduce to input the value of admixture from 0.45 % to 0.40% and increased water for required work ability.
But some times segregation and non-cohesive noticed.
Because while submitting re-conciliation report, it will be a problem for me.
Regards,
Vidhyasagar.
When the discharge of admixture is measured in liter per sec you need to do following thing.
Ensure, only single type of admixture is used for all concrete as the density, viscosity and specific gravity are not same for all type of admixture.
The calibration of dispencing motor should be done by pumping Admixture through it as per set value and verifying it by collecting the discharge on other end.
To do the above you should know the specific gravity / density of admixture.
Water have specific gravity of 1 or density of 1000 kg/cum so it can b easily reconcile as the ration of weight to volume is same
i.e. - 1 liter discharge leads to 1kg of discharge
in case of admixtures, the specific gravity/ density plays important role in measurements.
example : admixture have specific gravity of 1.2 or density of 1200kg/cum
So when i say its 1 cum it is actually 1200kg and not 1000Kg
same way 1 liter corresponds to 1.2 Kg
So in order to calibrate and pour the correct quantity of admixture in concrete.
You need to convert admixture weight to liters (as the motor only measures / dispense flow in liter per sec) and then you should first calibrate it.
Example - I set 1 liter and dispense it in auto mode, collected the flowed quantity of admixture and measured its weight + volume.
same way repeated up to max quantity of admixture dispensed in a batch of concrete + 1 Liter.
After doing the calibration and finding the consistent results you can dose admixture without any worry.
Hope the above details will help you in identifying the issue.